Re: White soot


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 4 ] [ FAQ ]

Posted by sid on February 01, 2006 at 06:10:05:

In Reply to: White soot posted by Angus on February 01, 2006 at 02:58:45:

: I have a Cleaver Brooks #2 oil fired fire tube boiler. When the back door was removed for the annual cleaning It had alot of white soot from just inside the combustion chamber, on the tube sheet, and extended to about a foot inside of the second pass. It has a consistency of sodium. I have not been able to get an explanation as to what it may be. Our boiler rep tells me I need to have it analized in a lab if I really need to know. I have never run across it before. This boiler also runs with a positive draft most of the time (when >60 % F.R.) and the stack temperature is low, about 190 F. This is the way our boiler rep wants it to run. We also have alot of stack condensation. I'm wodering if anyone has seen this kind of soot before and could it be a result of an underfired boiler. Thanks.
Are you using a low sulfur fuel , and are you using any fuel oil treatment . Plus what is you O2 range . How you are running a 190 stack temp . just does sound right .We run CB200-500 and are stack temp. is between 250 and 340 on natural gas and 300 to 350 on #2 oil and thats after or econ.We white spots that if have see are from soot that then is fired off . if it starts black and then trues white its that . or maybe high surfur in your fuel