[an error occurred while processing this directive]

Re: Combustion control of wood-waste & natural gas boiler


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 3 ] [ FAQ ]

Posted by Cesar on November 11, 2003 at 12:06:17:

In Reply to: Re: Combustion control of wood-waste & natural gas boiler posted by Pete on November 10, 2003 at 15:34:20:

Yes, it's currently on DCS.
When the boiler reaches a steady state producing 30 to 40 tph the gas burner can be turned off. The operators of the plant burn gas to elevate the steam production of the boiler when sudden demands occur and in the boiler startup.

: :Is your plant on dcs control?

: Do you need to burn gas to support combustion?

: I would strive to eliminate the use of gas altogether, only to be used as a back-up fuel. If you have dry wood waste this should be achievable.
: If this is not possible, take the fuel flow controller out of the boiler master control loop. Run it at a minimum setting.