Re: Bottom blowdown on low pressure boilers


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 2 ] [ FAQ ]

Posted by WLC on July 16, 2001 at 23:53:29:

In Reply to: Bottom blowdown on low pressure boilers posted by RTB on June 28, 2001 at 10:34:27:

: I am looking for the section of boiler and pressure vessel code that discusses the requirements for bottom blowdown on boilers less than 300 psig. From my understanding, this blowdown must be manual but I can't find where it is in the code. I recognize that automated bottom blowdown culd be dangerous if the blowdown vavle locks open, but on something lide a firetube boiler the buners will trip on low level and the temperatures are relatively low. Can someone direct me to the part of the code that specifically says you can't put a timed blowdown on the bottom of a low pressure heat exchanger? Thanks in advance.

Not expert on code and I have only been in the business for two years.
However I have seen LWCO's fail. I have seen main gas valves stick open.
I have seen motorized and solenoid operated water valves stick open.
If LWCO or main gas valve are not working right and automatic bottom
blow down causes a low water condition you can have a major waterside EXPLOSION!