Re: PRV STATION


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 4 ] [ FAQ ]

Posted by Joe Lambert on March 23, 2009 at 07:11:52:

In Reply to: PRV STATION posted by BOBMARC on March 18, 2009 at 20:55:37:

The best word is SLOWLY. Other than that, you did not give enough information on the PRV station, like inlet/outlet pressures, regulators or control valves, one cut or two??
Basically, you want to open valves very slowly and let all water/condensate out of the system through the traps, and even double check that you are getting live steam at the trap point through a strainer blowdown or valve. It is warming up the pipe and avoiding water hammer that is most important. Then, when all is hot you can set the pressures....


Follow Ups:



Post a Followup