Re: Apartment Building Boiler Questions


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 2 ] [ FAQ ]

Posted by Tom Stanton on March 12, 2002 at 10:01:25:

In Reply to: Apartment Building Boiler Questions posted by Lenny on March 11, 2002 at 17:31:59:

1. Watts is very common, probably the most widley used.

2. No problem adding water with the boiler is in operation, the make-up connection is typically connected to the return side of the boiler. This is usually done automatically through a reducing valve.

3. What is the MAWP of the boiler? If it's 30 psi, then the pressure during operation should be about 22- 25 give or take a little. It the MAWP is higher naturally the pressure will be higher.

4. If you getting a lot of sediment in the system try bottom blowing the boiler. If this is a steel boiler and you add chemicals you MUST blow down the boiler otherwise you will have huge problems.