Posted by Tarzan on June 16, 2001 at 05:24:01:

In Reply to: Re: Lighting Strike-HELP ! posted by Harold Kestenholz - Hydronic Network on June 15, 2001 at 15:03:42:

: Seems like time to break out the spare control and bring this one down to the control supplier for a sequencing test.

Old style Honeywell...rotating disc type...got the book out, took the covers off and observed as it rotated...timed the events as described in the book...watched the relays click in and out thru the sequence...no joy there...

Started at the top and began working down checking all switches and interlocks with ohm meter and blew out all sensing lines, changed out complete fire eye and amp...swapped honeywell with standby boiler...swapped all panalarm cards from standby boiler-firing standby with each swap...

K4 relay on honeywell won't pull in on startup, has to be pulled in by hand as reset/lock out button won't do it...once boiler gets thru purge cycle, it pops out along with relay next to purge cycle timer...finally found the blueprints for the flame safeguard ladder...

I love it, gives me something to do....