re: boiler contamination


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 2 ] [ FAQ ]

Posted by Scott on April 23, 2001 at 14:47:47:

Vern, The readings are for the boilers except for the condensate cond. and the FW cond.. The condensate is taken from the return line to the deaerator and the feedwater is from the deaerator. When contaminated the F.W. and condensate condutivity are high. The blr. conductivity stays in range w/o excess blowdown. The header pressure is 100 psi. Drum press. is 110-125 depending on the load. Condensate has not been checked for sulf. or phosphate. All the heat exchangers are ok. Thanks


Follow Ups:



Post a Followup

Name:
E-Mail:

Subject:

Comments:


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 2 ] [ FAQ ]