Posted by Bill on August 28, 2004 at 12:01:30:
In Reply to: Re: White Rodgers Aquastat posted by HeatProi on August 28, 2004 at 11:20:43:
: Now you need to determine:
: Is the sensor reading properly because the space between the sensor is not occupied by a better spacing metal than the paste alone?
: Did you turn the high limit to 150 or the low limit?
: Is the aquastat OK?
: Also, why set a triple aquastat to 150F when the minimum temperature for making hot water should be 180F and the water temperature limited by a tempering valve?
The aquastat is brand new, do they frequently come broken?
Also, I set it for 150 because thats the spot where it shut the boiler off when the water is actually 210. I get plenty of hot water, the circulator kicks on when the thermostat calls, and the boiler goes on at 180 and off at 210.